    Default Question for the experienced sparkies (electricians)

    First of all,.. Are there any experienced and knowledgeable electricians on beyond?

    Bunch of questions regarding moving a meter box and wire guage.

    Additional notes:
    - Inner city property with overhead power
    - 100 yr old home with meter in the house.
    Current meter is 100a, although main throw is 30a (looks to be 100 yrs old, located before the meter - yes it would be super easy to steal power)
    Oldish panel after meter - 100a


    So here is my situation, I have an old meter in my kitchen.

    I've set up the new meter base (100a) on the outside of the house.
    Conduit up the side right to where the line feeds into the original wires.

    Now, I've already run 3ga wire up the conduit (2xblack and 1xwhite).

    After I run the wires I took a look at the meter base and there is only 1 mounting spot for the black.
    I've checked out all meter bases available at the local home depot (thinking i picked up the wrong one) and they are all the same.

    For 100a service, is only 1 black wire required from the line in?

    How does enmax attach 2x3ga blacks in one spot that looks just big enough for 1x3ga wire.

    Or.... Did I go over kill and 6ga wire should be run down the conduit from the line in to the base?

    Am I off my rocker thinking there should be 2xblacks and 1xwhite coming in?

    Lastly, am I in over my head? (non-trades people need not answer)




    Yes, I did bury a grounding plate 2' in the ground with 3ga ground wire running to the base.
    Last edited by barmanjay; 08-19-2012 at 10:01 PM.
    Burn some serious rubber on your Wedding Night!!


    Renovating a home the hard way:
    http://propertysensei.wordpress.com/

  2. #2
    Join Date
    Nov 2003
    Location
    Vernon, BC
    My Ride
    2017 Golf TSI
    Posts
    2,463
    Rep Power
    23

    Default

    Sounds like you bought a single phase meter base to me
    Originally posted by Vagabond142
    Is the best game. Ever. In everness. It is more awesome than a robot caveman punching God in the dick. It is that awesome

  3. #3
    Join Date
    Mar 2004
    Location
    Calgary
    My Ride
    300C srt8, Venza, F150, Expedition
    Posts
    1,435
    Rep Power
    22

    Default

    Ok, I just re-read all the literature I've saved.

    Seems I am ok with the 3x 3ga wire sizes and the meter box seems right.

    My conventional brain of how the wires should be hooked up is wrong.
    (thinking black on one side, white on the other)

    The meter base does infact have 3 places to hook up the wires and a separate ground.

    The blacks go on the outside connectors and the white goes in the middle.

    Here is a pic (not of my actual meter base) of an example.

    click for larger version
    » Click image for larger version


    I think I just needed to clear my mind a bit.
    Burn some serious rubber on your Wedding Night!!


    Renovating a home the hard way:
    http://propertysensei.wordpress.com/

  4. #4
    Join Date
    Nov 2003
    Location
    Vernon, BC
    My Ride
    2017 Golf TSI
    Posts
    2,463
    Rep Power
    23

    Default

    Yeah sounds like you've got it nailed down now. Basically the neutral (which is also earthed very nearby) passes straight through and both lines are interrupted until the meter is fitted, so from left to right, line, neutral, line.

    AFAIK #3 wire is fine for 100A service use even in conduit, and everything you are connecting it to should be sized for much bigger so you should have no problems with it fitting in terminals and such.

    From the initial description it sounded like you had a single phase meter base, I was wondering just where the hell you found one of those in a retail store
    Originally posted by Vagabond142
    Is the best game. Ever. In everness. It is more awesome than a robot caveman punching God in the dick. It is that awesome

  5. #5
    Join Date
    Mar 2004
    Location
    Calgary
    My Ride
    300C srt8, Venza, F150, Expedition
    Posts
    1,435
    Rep Power
    22

    Default

    I thought I had a single phase too.

    Needed to let my head clear before looking at the meter again and the literature.

    My mind was filled with the basic visual of an outlet.


    Although, the meter that is currently in my kitchen i believe is a single phase.

    Looks to be like an 8 ga line on it aswell. Go figure?

    1 Blk + 1 wht in
    1 Blk + 1 wht out



    Time to finish up the rest of my electrical then hope for the city 'approval'.
    Burn some serious rubber on your Wedding Night!!


    Renovating a home the hard way:
    http://propertysensei.wordpress.com/

  6. #6
    Join Date
    Apr 2003
    Location
    Calgary
    Posts
    155
    Rep Power
    0

    Default

    you have single phase power. 2 hot leads and one ground lead. 120/240. Do you have a permit?
    1990 Poonstang
    1990 Sexplorer
    1967 Chevelle Panty Dropper
    2003 GMC SLE 1500HD Donkey Hauler
    2013 Ram Longhorn w/ a 6" lift and 35s
    2017 Nissan Maxima

  7. #7
    Join Date
    Nov 2003
    Location
    Vernon, BC
    My Ride
    2017 Golf TSI
    Posts
    2,463
    Rep Power
    23

    Default

    Originally posted by colinderksen
    you have single phase power. 2 hot leads and one ground lead. 120/240. Do you have a permit?


    Single phase is 1 hot + 1 grounded (or neutral if you prefer), he does not have single phase.

    Enmax wouldn't be doing the service switchover if he didn't have a permit. Why did you even post?...
    Originally posted by Vagabond142
    Is the best game. Ever. In everness. It is more awesome than a robot caveman punching God in the dick. It is that awesome

  8. #8
    Join Date
    Mar 2004
    Location
    Calgary
    My Ride
    300C srt8, Venza, F150, Expedition
    Posts
    1,435
    Rep Power
    22

    Default

    Originally posted by Zero102




    Single phase is 1 hot + 1 grounded (or neutral if you prefer), he does not have single phase.

    Enmax wouldn't be doing the service switchover if he didn't have a permit. Why did you even post?...

    Yup

    Enmax won't even touch it until there is a green sticker from the city,.. Still lots more work for me to do on other places before I can do that.
    Burn some serious rubber on your Wedding Night!!


    Renovating a home the hard way:
    http://propertysensei.wordpress.com/

  9. #9
    Join Date
    Oct 2005
    Location
    Medicine Hat/Calgary
    My Ride
    toyotas, mitsu, and a ford
    Posts
    370
    Rep Power
    19

    Default

    Originally posted by Zero102




    Single phase is 1 hot + 1 grounded (or neutral if you prefer), he does not have single phase.

    Enmax wouldn't be doing the service switchover if he didn't have a permit. Why did you even post?...
    He certainly does have single phase. Its a edison 3 wire circuit 120/240. 3 phase would be 120/208 (all 3 phase derivatives have to be 1.73 higher eg 277/480 347/600) as well 3 phase services have to have 3 hots and may contain a neutral (it wont if its fed from a delta/delta or wye/delta transformer)

    Edison 3 wires circuits are 2 sine waves 180degrees apart where 3 phase is always 3 waves 120 degrees apart.

  10. #10
    Join Date
    Nov 2003
    Location
    Vernon, BC
    My Ride
    2017 Golf TSI
    Posts
    2,463
    Rep Power
    23

    Default

    Originally posted by Crazyjoker77


    He certainly does have single phase. Its a edison 3 wire circuit 120/240. 3 phase would be 120/208 (all 3 phase derivatives have to be 1.73 higher eg 277/480 347/600) as well 3 phase services have to have 3 hots and may contain a neutral (it wont if its fed from a delta/delta or wye/delta transformer)

    Edison 3 wires circuits are 2 sine waves 180degrees apart where 3 phase is always 3 waves 120 degrees apart.
    I never said he has 3 phase power.

    In a typical household supply there are 2 ungrounded conductors that are 180* out of phase. When one is +168V the other is -168V relative to ground. That is 2 phases not one. Lots of people call this single phase power but really it isn't. Single phase would be all ungrounded conductors rising and falling in time. If he had single phase 120/240 then one would 168V while the other was 376V relative to ground, and that is not what we have.
    Originally posted by Vagabond142
    Is the best game. Ever. In everness. It is more awesome than a robot caveman punching God in the dick. It is that awesome

  11. #11
    Join Date
    Oct 2005
    Location
    Medicine Hat/Calgary
    My Ride
    toyotas, mitsu, and a ford
    Posts
    370
    Rep Power
    19

    Default

    Originally posted by Zero102


    I never said he has 3 phase power.

    In a typical household supply there are 2 ungrounded conductors that are 180* out of phase. When one is +168V the other is -168V relative to ground. That is 2 phases not one. Lots of people call this single phase power but really it isn't. Single phase would be all ungrounded conductors rising and falling in time. If he had single phase 120/240 then one would 168V while the other was 376V relative to ground, and that is not what we have.
    again you are wrong it is still considered single phase. both sine waves DO NOT have to rise together but they both must cross 0 at the same time. Polarity are different between them but they are IN phase with each other.



    where as 3phase there is actually a phase difference.



    and a quote from basic 3 phase principles in 3rd year module to better word it.

    "You may think think there are two 120v phases in a single-phase service, however there are not. the voltage of L1 to neutral is the voltage of only half of one winding and the voltage of neutral to L2 is the voltage of the other half of that single winding. The rise and fall of the sine wave values of voltage from L1 to Neutral occur at the same time as as the rise and fall of sine wave values of voltage from L2 to neutral. Their peak values can be different , but they are in phase (or in time)with each other. A two pole breaker can be connected to the two live conductors from that single transformer winding, but it is still a single phase, not a two phase, circuit.

    This is a two phase waveform.


    now please go hand in your ticket if you even have one.

  12. #12
    Join Date
    Nov 2003
    Location
    Vernon, BC
    My Ride
    2017 Golf TSI
    Posts
    2,463
    Rep Power
    23

    Default

    Wow, that got personal real fast

    The OP's issue has been solved and this thread is not only derailed but deteriorating quickly.
    Originally posted by Vagabond142
    Is the best game. Ever. In everness. It is more awesome than a robot caveman punching God in the dick. It is that awesome

  13. #13
    Join Date
    Jul 2003
    Location
    Here
    My Ride
    is wild
    Posts
    1,095
    Rep Power
    22

    Default

    Originally posted by Zero102




    Single phase is 1 hot + 1 grounded (or neutral if you prefer), he does not have single phase.

    Enmax wouldn't be doing the service switchover if he didn't have a permit. Why did you even post?...

    Originally posted by Zero102
    Wow, that got personal real fast

    The OP's issue has been solved and this thread is not only derailed but deteriorating quickly.
    Wow you certainly shouldnt be giving electrical wiring advice. Let me guess still in school?
    .

    Reasons why Drumheller area wouldn't make a good race track venue...

    Originally posted by Agera_56
    My wife likes to shop but, I'm sorry, Drumheller isn't going to cut it in that regard (sorry guys, but honestly, if she's happy, I'm happy).

  14. #14
    Join Date
    Apr 2009
    Location
    The Peoples Republic of Albertastan
    Posts
    5,245
    Rep Power
    20

    Default

    .
    Last edited by Cos; 12-20-2016 at 10:28 PM.
    Originally posted by adam c

    Line goes up, line goes down, line does squiggly things and fucks Alberta
    "The stone age didn't end because we ran out of stones"

  15. #15
    Join Date
    Jul 2004
    Location
    Calgary
    My Ride
    2010 frontier pro-4x
    Posts
    565
    Rep Power
    20

    Default

    120/240 is definatley single phase still and barman your meter looks good. It is very easy to over think electrical.

  16. #16
    Join Date
    Oct 2009
    Location
    Calgary
    Posts
    1,198
    Rep Power
    0

    Default

    Wow. And I thought MY trade was complicated! All I have to worry about is "shiny side up".

  17. #17
    Join Date
    Apr 2009
    Location
    The Peoples Republic of Albertastan
    Posts
    5,245
    Rep Power
    20

    Default

    .
    Last edited by Cos; 12-20-2016 at 10:28 PM.
    Originally posted by adam c

    Line goes up, line goes down, line does squiggly things and fucks Alberta
    "The stone age didn't end because we ran out of stones"

  18. #18
    Join Date
    Apr 2009
    Location
    The Peoples Republic of Albertastan
    Posts
    5,245
    Rep Power
    20

    Default Re: Question for the experienced sparkies (electricians)

    .
    Last edited by Cos; 12-20-2016 at 10:28 PM.
    Originally posted by adam c

    Line goes up, line goes down, line does squiggly things and fucks Alberta
    "The stone age didn't end because we ran out of stones"

  19. #19
    Join Date
    Mar 2004
    Location
    Calgary
    My Ride
    300C srt8, Venza, F150, Expedition
    Posts
    1,435
    Rep Power
    22

    Default

    Well

    This is interesting stuff, trying to understand the waves is surely confusing.



    Here is a question then.

    The existing meter is supplied with only 2 wires. The overhead lines: the third wire is taped off.

    Is this still considered single phase? What would the wave look like?


    Can't reverse the wires otherwise I blow the main fuse (screw in fuse).


    Cos:

    Im assuming I can do this under a homeowners permit, but this is the main and I definitely want an electrician to come and check it now.

    As competent as I am with being handy and skillful, my knowledge is limited to reading material and no practical experience with power mains/meters.

    Roughing in household wires, I feel I can do those blindfolded.
    Last edited by barmanjay; 08-25-2012 at 10:03 AM.
    Burn some serious rubber on your Wedding Night!!


    Renovating a home the hard way:
    http://propertysensei.wordpress.com/

  20. #20
    Join Date
    Apr 2009
    Location
    The Peoples Republic of Albertastan
    Posts
    5,245
    Rep Power
    20

    Default

    .
    Last edited by Cos; 12-20-2016 at 10:27 PM.
    Originally posted by adam c

    Line goes up, line goes down, line does squiggly things and fucks Alberta
    "The stone age didn't end because we ran out of stones"

Page 1 of 2 1 2 LastLast

Similar Threads

  1. Experienced Renters - Question for you

    By 2Legit2Quit in forum Real Estate / Finance
    Replies: 42
    Latest Threads: 04-27-2015, 02:24 PM
  2. Electricians question for you on heated flooring

    By Asian_defender in forum Home and Garden
    Replies: 7
    Latest Threads: 07-03-2014, 09:48 AM
  3. Car lift and Eletrical question (Electricians please look)

    By 00redLUDE in forum General Car/Bike Talk
    Replies: 9
    Latest Threads: 09-19-2010, 11:38 AM
  4. Replies: 22
    Latest Threads: 05-10-2007, 05:48 AM
  5. Replies: 0
    Latest Threads: 04-16-2007, 10:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •