So much misinformation! Must resist.... Just a couple points.
I will say one thing - for those of you who think this is a "pipe blowout" you couldn't be more wrong.
These types of leaks happen as a pinhole on a weld, likely on an elbow UNDER insulation. It will drip, then slowly piss and finally "let go" and it won't be larger than say a toonie or if it's a crack a pencil.
Also, it's not like this is a transportation "pipeline". It's a produced fluid return header from the well pads. It has back pressure from the front end treaters and the wells on the back. You do not notice a drop in production header pressure unless it is a true blow out. Such a blow out will never truly happen on the line as pipe leaks don't work like that - unless you have water/steam hammer which you would not within this line. It's always hot normally when the plant is up.
The DCS may or may not have interlocks for ESD's due to a low production header pressure condition. Most likely just an alarm for the control room to investigate and send a field operator to physically look.
What bugs me is the lack of redundancy in their physical checks. They should have the wellhead field operator doing 2-3 well site and line rounds, the team lead should also do this, followed by maintenance EVERY SHIFT. Obviously they didn't, or didn't look to hard.
"The most merciful thing in the world, I think, is the inability of the human mind to correlate all its contents... some day the piecing together of dissociated knowledge will open up such terrifying vistas of reality, and of our frightful position therein, that we shall either go mad from the revelation or flee from the light into the peace and safety of a new Dark Age."