lights are on 20a or less and 120v....Originally posted by FraserB
Lights are excluded. AFCI is only needed on circuits supplying 125V outlets rated 20A or less
lights are on 20a or less and 120v....Originally posted by FraserB
Lights are excluded. AFCI is only needed on circuits supplying 125V outlets rated 20A or less
seems like there's conflicting opinions between inspectors, even they are confused with the afci thing lol
A light is not an outlet though.Originally posted by gimp
lights are on 20a or less and 120v....
See Crank. See Crank Walk. Walk Crank Walk.
code says receptacles thoughOriginally posted by FraserB
A light is not an outlet though.
im not seeing in the 2015 CEC anything about lights being excluded, i'd actually like to have clarification on this
Ya... Receptacles, no lights.
I put all my Receptacles on a circuit by themself protected by the dead face AFCI. Then I put the entire bedroom circuit on an AFCI protected circuit. The bathroom is on its own circuit and will have a GFCI receptacle, and the rest of the lights are on their own regular breaker. .
Inspection tmw... We'll see what happens lol
Good luck tomorrow. Did you require a building permit before you applied for your electrical permit?
sig deleted by moderator, click here for info
Well the only thing he didn't like was my access to my panel. . I had to put in a 24" door in the bedroom to provide a clear path to the breaker. . That sucked... Removing the anchored down bottom plate framing... Moving a stud.... Moving electrical and data boxes and lines, having to re-run the wires because they were too short
Also had to change out the speaker wire because I didn't buy 'in-wall' wire
The inspector did want my bathroom receptacle on a AFCI circuit as well but I argued a little bit with him. . I told him I was going to put in a GFCI receptacle and I thought the bathroom is one of the exceptions. . He considered it and felt like he was okay with that and let it go lol
My inspection is tomorrow (garage and new underground electrical service), I'll post up what they say and probably make a new thread.
See Crank. See Crank Walk. Walk Crank Walk.
...
Last edited by Sugarphreak; 08-15-2019 at 08:17 PM.
Passed inspection, inspector was here less than 10 minutes.
He also confirmed that lights on a non-AFCI circuit by themselves would be acceptable under code.
See Crank. See Crank Walk. Walk Crank Walk.