  1. #21
    Join Date
    Oct 2002
    Location
    Calgary
    My Ride
    Corvette
    Posts
    587
    Rep Power
    22

    Default

    Just adding to the list of others past couple days; exact same issue and error code, cleared the outside vents and it was back to normal shortly thereafter.

  2. #22
    Join Date
    Jun 2003
    Location
    Calgary
    My Ride
    KTM
    Posts
    857
    Rep Power
    21

    Default

    Have the same issue. Is there a fix for this aside from unclogging it every time it snows? I have heard of some people making the intake a "T" rather then terminating straight out. Any suggestions?

  3. #23
    Join Date
    Jan 2014
    Location
    Airdrie
    My Ride
    '16 WRX, '23 CX-50
    Posts
    447
    Rep Power
    12

    Default

    So the intake for my furnace was installed as a T, where the exhaust is just a J bend pointed exhausting towards the ground. Going to try the same with the HWT in the summer.

  4. #24
    Join Date
    Jun 2003
    Location
    Calgary
    My Ride
    KTM
    Posts
    857
    Rep Power
    21

    Default

    Installed a T today on mine, will post up results

  5. #25
    Join Date
    Aug 2017
    Location
    'Berta
    My Ride
    A bunch of Nissans..duh.
    Posts
    312
    Rep Power
    7

    Default

    Quote Originally Posted by craigcd View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Have the same issue. Is there a fix for this aside from unclogging it every time it snows? I have heard of some people making the intake a "T" rather then terminating straight out. Any suggestions?
    Mine is a T for exhaust and J for intake, the T still developed icicles that tripped the sensors and the intake builds up Frost like crazy.... Thank God it only happens when it's really cold...I also don't have houses beside me until three lots over..

  6. #26
    Join Date
    Jun 2003
    Location
    Calgary
    My Ride
    KTM
    Posts
    857
    Rep Power
    21

    Default

    Quote Originally Posted by NissanFanBoy View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Mine is a T for exhaust and J for intake, the T still developed icicles that tripped the sensors and the intake builds up Frost like crazy.... Thank God it only happens when it's really cold...I also don't have houses beside me until three lots over..
    Ya they did the T for my furnace intake but not the water heater. I dont get it. Been working fine since install but it hasn't snowed / there hasn't been a bunch of snow blowing. I am sure next time I am in a rush to get somewhere and jump in the shower in a hurry it will be freezing cold

    Nothing worse than starting your day with a freezing shower!

  7. #27
    Join Date
    May 2004
    Location
    cgy
    Posts
    598
    Rep Power
    20

    Default

    Quote Originally Posted by craigcd View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Installed a T today on mine, will post up results
    Did this work for you? Mine got clogged up 3 times within 24 hours yesterday... 3pm, 7pm, and then 4am.


  8. #28
    Join Date
    Sep 2002
    Location
    BoostLand
    My Ride
    something green
    Posts
    1,931
    Rep Power
    28

    Default

    Every cold snap, it brings to light how condensing appliances should be a choice rather than the law. The design really doesn't lend itself to cold snaps, and the longer the cold snap the worse it gets. ive been doing 8-10 service calls a day since before xmas most of the calls end up being frozen intakes, sensing tubes, exhaust pipes, which in turn meant frozen structures with frozen condensing appliances. Number of calls I did on appliances with atmospheric burners and thermocouples, zero and about a 1/3rd of my customers still have that level of appliance. My own appliances are all Tc atmospheric.
    What I end up doing on a lot of installs is getting an oversize box made for the intake with mesh pointing down, rather than relying on the intake pipe sized mesh not to frost up. And if your exhaust points straight up, you need to make sure the cycle of the appliance is long enough to get the pipe warm to allow the condensate in the pipe to run back to drain. Short cycles result in exhaust pipe blockage.
    Too loud for Aspen

  9. #29
    Join Date
    Jun 2003
    Location
    Calgary
    My Ride
    KTM
    Posts
    857
    Rep Power
    21

    Default

    Quote Originally Posted by wildrice View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Did this work for you? Mine got clogged up 3 times within 24 hours yesterday... 3pm, 7pm, and then 4am.
    I havent clogged since install!

  10. #30
    Join Date
    Jun 2009
    Location
    N/A
    Posts
    2,977
    Rep Power
    22

    Default

    Quote Originally Posted by Maxt View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Every cold snap, it brings to light how condensing appliances should be a choice rather than the law. The design really doesn't lend itself to cold snaps, and the longer the cold snap the worse it gets. ive been doing 8-10 service calls a day since before xmas most of the calls end up being frozen intakes, sensing tubes, exhaust pipes, which in turn meant frozen structures with frozen condensing appliances. Number of calls I did on appliances with atmospheric burners and thermocouples, zero and about a 1/3rd of my customers still have that level of appliance. My own appliances are all Tc atmospheric.
    What I end up doing on a lot of installs is getting an oversize box made for the intake with mesh pointing down, rather than relying on the intake pipe sized mesh not to frost up. And if your exhaust points straight up, you need to make sure the cycle of the appliance is long enough to get the pipe warm to allow the condensate in the pipe to run back to drain. Short cycles result in exhaust pipe blockage.
    Condensing appliances are the law?

    So if my 80's era furnace conks out, I can't replace it with something similar?

    What about my water heater? I replaced it myself a number of years ago (6 or so) and it's not a HE appliance - it vents up our regular chimney. Would the next one have to be HE?
    Will fuck off, again.

  11. #31
    Join Date
    Jun 2003
    Location
    Calgary
    My Ride
    KTM
    Posts
    857
    Rep Power
    21

    Default

    Quote Originally Posted by speedog View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Condensing appliances are the law?

    So if my 80's era furnace conks out, I can't replace it with something similar?

    What about my water heater? I replaced it myself a number of years ago (6 or so) and it's not a HE appliance - it vents up our regular chimney. Would the next one have to be HE?
    Not sure about the furnace but a had a friend hire a plumber to install a water heater last month and he also opted for a non HE water heater. It seems like its not an issue?

  12. #32
    Join Date
    Nov 2008
    Location
    Cochrane, AB
    My Ride
    Trucks
    Posts
    2,119
    Rep Power
    43

    Default

    Mid efficient furnaces have been discontinued for a number of years, so law or not, they are not being manufactured. I'm sure water heaters will happen eventually (in decades?) but the energy savings potential for a high efficiency water heater is not as good.

  13. #33
    Join Date
    Sep 2002
    Location
    BoostLand
    My Ride
    something green
    Posts
    1,931
    Rep Power
    28

    Default

    I was surprised to find out mid efficient is still available in the US, its just illegal to bring them into Canada. I was talking to a US equipment rep about an issue with condensing furnaces. When the high's are installed in sealed cabinet ventilation systems in portable structures in place of the original midefficient, the condensate drain tubes and collector pan freeze off. His response was "thats why we still make mid efficients for applications like that, and why Canadian efficiency rules are stupid". I asked if there was a resistance heater I could install in the furnace cabinet, and he said that the Canadian market isn't large enough to warrant paying for the approvals to do something like that. So we have to buy condensing furnaces, but our market really isn't large enough for the manufacturers to make our furnaces different just for us and we install them into conditions and climats where they don't function all that well.. But hey, look how green you're being..
    If you lived up north 6 miles west of Hairlip,population 143, what furnace would you rather have? I'd take the simplist most generic damn thing I could find...
    Too loud for Aspen

  14. #34
    Join Date
    Jan 2004
    Location
    Calgarian Living in Edmonton
    My Ride
    93 240sx SE, 17 Infiniti Q50S, 2008 Highlander
    Posts
    6,688
    Rep Power
    35

    Default

    Hijack thread. Seems like whenever the temps dip to really extreme temps, my vent stack is freezing up causing the toilet to gurgle/gasp for air when its flushed. How do I combat this?
    Originally posted by GTS Jeff
    You know those bored stay at home moms who's entire lives revolve around driving their kids to soccer, various cleaning accessories, and worrying about neighbourhood rapists? The kind of people that watch the View and go "uh huh..." Those unfulfilled people who try to fill the void in their empty lives by writing whiny letters to the editor complaining about shit that no one really cares about?

    Well imagine if instead of writing that letter to the editor, she just posts on a car forum for car enthusiasts. That's Kritafo.

  15. #35
    Join Date
    May 2002
    Location
    Calgary
    My Ride
    Hybrid
    Posts
    1,147
    Rep Power
    28

    Default

    Bump.
    My hot water heater intake pipe is frosting up in this weather... Intake and exhaust are roughly 1' apart, both have a 90° elbow pointing them downwards but the intake has an extra ~18" section of pipe after the elbow (presumably to try to prevent exhaust from being sucked in, also makes it a bitch to clear out the frost). Neither has mesh. Is there an accepted fix or best practice for venting that I can have the builder implement to resolve this? Never had this issue in 10 years at my old house.
    Originally posted by max_boost
    Hey baller, any problem money can solve is no problem at all. Don't sweat it.

  16. #36
    Join Date
    Jun 2002
    Location
    Calgary, AB
    Posts
    1,991
    Rep Power
    30

    Default

    Don't know how to fix it but a coat hanger works good to clear it.

  17. #37
    Join Date
    Sep 2018
    Location
    Edmonton, Alberta
    Posts
    536
    Rep Power
    16

    Default

    Quote Originally Posted by Strider View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Bump.
    My hot water heater intake pipe is frosting up in this weather... Intake and exhaust are roughly 1' apart, both have a 90° elbow pointing them downwards but the intake has an extra ~18" section of pipe after the elbow (presumably to try to prevent exhaust from being sucked in, also makes it a bitch to clear out the frost). Neither has mesh. Is there an accepted fix or best practice for venting that I can have the builder implement to resolve this? Never had this issue in 10 years at my old house.
    If you've never had the issue before, then it is likely just do to a temporary condition of the wind/temperature. I've had this happen in an old house after I built my fence, I spent a couple bucks on an elbow and a few inches of PVC. Didn't even glue it in place. I would just go jam it on when it would cold enough for the intake to freeze up. Pulling air from a different direction, or farther from the exhaust heat would clear it right up. Otherwise I would be out clearing it at least once a day when it was minus 30.

  18. #38
    Join Date
    May 2002
    Location
    Calgary
    My Ride
    Hybrid
    Posts
    1,147
    Rep Power
    28

    Default

    Quote Originally Posted by roopi View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Don't know how to fix it but a coat hanger works good to clear it.
    I didn't think I could do a reasonable job scraping the whole inside diameter with a wire coat hanger, especially around the elbow, so I was jamming in a rolled up towel. Ordered a heat gun from Amazon same day for today in case it frosts up again.

    Quote Originally Posted by Misterman View Post
    This quote is hidden because you are ignoring this member. Show Quote
    If you've never had the issue before, then it is likely just do to a temporary condition of the wind/temperature. I've had this happen in an old house after I built my fence, I spent a couple bucks on an elbow and a few inches of PVC. Didn't even glue it in place. I would just go jam it on when it would cold enough for the intake to freeze up. Pulling air from a different direction, or farther from the exhaust heat would clear it right up. Otherwise I would be out clearing it at least once a day when it was minus 30.
    Not sure if it wasn't clear, it was at my old house where I never had this issue. We just moved into our new house in Oct and we're having this issue (among others) with the first cold snap. Another elbow and some PVC could probably do the trick, but I'd rather have a permanent solution than a band-aid at 1am in -30° weather after a cold shower.
    Originally posted by max_boost
    Hey baller, any problem money can solve is no problem at all. Don't sweat it.

  19. #39
    Join Date
    Sep 2018
    Location
    Edmonton, Alberta
    Posts
    536
    Rep Power
    16

    Default

    Quote Originally Posted by Strider View Post
    This quote is hidden because you are ignoring this member. Show Quote



    Not sure if it wasn't clear, it was at my old house where I never had this issue. We just moved into our new house in Oct and we're having this issue (among others) with the first cold snap. Another elbow and some PVC could probably do the trick, but I'd rather have a permanent solution than a band-aid at 1am in -30° weather after a cold shower.
    The permanent solution is to either leave the added elbow in place, or make it part of your yearly winterizing schedule in the fall. There is no fix to your intake pulling in humid air at -30, the humidity will freeze.

Page 2 of 2 FirstFirst 1 2

Similar Threads

  1. Please service my Hot water tank-no hot water!

    By 540i in forum Home and Garden
    Replies: 2
    Latest Threads: 12-30-2012, 09:29 PM
  2. Hot Water Tank, no hot water.

    By Alterac in forum Home and Garden
    Replies: 12
    Latest Threads: 11-27-2009, 10:52 AM
  3. 17 year old robs 86 year old woman.

    By signature7 in forum Society / Law / Current Events / Politics
    Replies: 5
    Latest Threads: 11-14-2008, 06:34 PM
  4. 5 year old & 8 year old DJ's

    By Speed_69 in forum Misc. Gallery
    Replies: 12
    Latest Threads: 01-18-2008, 10:10 PM
  5. Error, Error, Error

    By finboy in forum Computers, Consoles, and other Electronics
    Replies: 9
    Latest Threads: 04-10-2004, 12:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •