    Default radiant heat, boilers and heat exchangers

    I have a 6 zone radiant heat system with a boiler attached.

    4 zones are for the basement, and 2 are for the garage.

    (The main floor and upper floors are forced air).

    I've noticed that in very cold temperatures, the radiant heat (in slab) in the basement struggles to keep up.

    Because the radiant heat is fed by poly-B in the basement, the system is two closed loops (not sure the terminology here). With the "boiler loop" isolated from the "radiant loop" that has all of the poly-B hosing in it. Sounds good- protected from oxygenation and corrosion.

    The problem seems to be that the average temperature of the water on the radiant side seems quite low, and the average temperature on the boiler loop seems quite high (70C vs around 40C). From what I can tell, the heat exchanger is not able to increase the radiant loop temperature enough in colder weather.

    Has anyone encountered this problem? Are there better heat exchangers? Do heat exchangers wear/corrode over time causing a degradation? Is this type of low efficiency common for a heat exchanger?

    Plumbers?

  2. #2
    Join Date
    Aug 2003
    Location
    Medicine Hat, AB
    Posts
    2,009
    Rep Power
    26

    Default

    Quote Originally Posted by Buster View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Do heat exchangers wear/corrode over time causing a degradation?
    They most certainly can given Calgary's hard water. They become calcified and can lose efficiency. You might be able to clean it or may require a replacement.

  3. #3
    Join Date
    Oct 2003
    Location
    Calgary
    My Ride
    ute
    Posts
    4,937
    Rep Power
    100

    Default

    Quote Originally Posted by spike98 View Post
    This quote is hidden because you are ignoring this member. Show Quote
    They most certainly can given Calgary's hard water. They become calcified and can lose efficiency. You might be able to clean it or may require a replacement.
    Thanks for the note. Do you recommend anyone in town that can inspect/service/clean/replace the exchanger?

  4. #4
    Join Date
    Nov 2002
    Location
    Not Aspen
    My Ride
    Two from Freemont
    Posts
    9,807
    Rep Power
    45

    Default

    Are your valves actually opening? I had to replace 2 valves recently for the Ensuite and secondary washroom floors. They were stuck open and only got heat when another zone demanded it.

    The system is closed, calcium deposits should remain static unless you have a leak and new water is being introduced (mo logic anyway). If you have a leak, that is a bigger problem as your Glycol will also start to be diluted as it leaks out.

    - - - Updated - - -

    Quote Originally Posted by Buster View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Thanks for the note. Do you recommend anyone in town that can inspect/service/clean/replace the exchanger?
    I went with Canyon Plumbing because they did the install. My last service / cleaning cost $2K with the valves.

  5. #5
    Join Date
    Oct 2003
    Location
    Calgary
    My Ride
    ute
    Posts
    4,937
    Rep Power
    100

    Default

    Quote Originally Posted by benyl View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Are your valves actually opening? I had to replace 2 valves recently for the Ensuite and secondary washroom floors. They were stuck open and only got heat when another zone demanded it.

    The system is closed, calcium deposits should remain static unless you have a leak and new water is being introduced (mo logic anyway). If you have a leak, that is a bigger problem as your Glycol will also start to be diluted as it leaks out.

    - - - Updated - - -



    I went with Canyon Plumbing because they did the install. My last service / cleaning cost $2K with the valves.
    I'm going to get up there with some masking tape and my IR thermometer to test. But I'm pretty sure they are functioning normally. The temperature of the water coming out of the heat exchanger on the "house/radiant" loop is quite low. 40C. The boiler loop temperature is close to 70C. So the delta-T between the boiler loop and the radiant loop is quite high.

  6. #6
    Join Date
    Jan 2008
    Location
    Upstairs
    My Ride
    Natural Gas.
    Posts
    13,332
    Rep Power
    100

    Default

    Quote Originally Posted by Buster View Post
    This quote is hidden because you are ignoring this member. Show Quote
    I'm going to get up there with some masking tape and my IR thermometer to test. But I'm pretty sure they are functioning normally. The temperature of the water coming out of the heat exchanger on the "house/radiant" loop is quite low. 40C. The boiler loop temperature is close to 70C. So the delta-T between the boiler loop and the radiant loop is quite high.
    What was that delta-t when the system was new?
    Quote Originally Posted by killramos View Post
    This quote is hidden because you are ignoring this member. Show Quote
    You realize you are talking to the guy who made his own furniture out of salad bowls right?

  7. #7
    Join Date
    Oct 2003
    Location
    Calgary
    My Ride
    ute
    Posts
    4,937
    Rep Power
    100

    Default

    Quote Originally Posted by ExtraSlow View Post
    This quote is hidden because you are ignoring this member. Show Quote
    What was that delta-t when the system was new?
    Good question...unfortunately it's pretty old, so I can't get that data. But a 30C delta-t is, I'm sure, WAY out of the exchanger's expected performance.

  8. #8
    Join Date
    Sep 2014
    Location
    Airdrie
    My Ride
    6.2 / 690
    Posts
    179
    Rep Power
    0

    Default

    Scaling probably. Acid wash that HX and you'll notice an improvement guaranteed
    Last edited by tcon; 02-13-2019 at 05:26 PM.

  9. #9
    Join Date
    Oct 2003
    Location
    Calgary
    My Ride
    ute
    Posts
    4,937
    Rep Power
    100

    Default

    I dont see any obvious way to isolate the exchanger to pull it off and do any maintenance to it. Given that it is almost acceptable in terms of performance, I'm wondering if I should wait until the weather is warmer before messing with it.

  10. #10
    Join Date
    Jan 2019
    Location
    The Big Char.
    My Ride
    *The First*
    Posts
    4,136
    Rep Power
    100

    Default

    "Poly-B" as in polybutylene plastic? It's leaking. That's what it does. That stuff is trash in an ideal scenario and when you stick it in concrete it's even worse. That and your exchanger is getting fouled with mineral deposits.
    Leave it until warmer and investigate then.
    -1 for Canyon Plumbing. They have some good people but they also have some failed coat hanger abortions who can't follow basic code for drain distances and will plumb a toilet with hot water. Your problem is too complex to risk the wrong simpleton showing up.

Similar Threads

  1. Service rig boilers

    By lil*tymer in forum Careers
    Replies: 2
    Latest Threads: 11-09-2011, 08:19 PM
  2. FS: radiant garage heater

    By gimp in forum Miscellaneous Buy/Sell/Trade
    Replies: 5
    Latest Threads: 02-07-2009, 11:04 AM
  3. FS: Mint Sega Saturn + Radiant Silvergun + a lot more...

    By eposer in forum Video Games / Consoles
    Replies: 7
    Latest Threads: 03-02-2007, 05:04 AM
  4. Thermostat for Radiant Heating?

    By Mixalot27 in forum General
    Replies: 5
    Latest Threads: 11-27-2006, 06:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •