    OK, I'll type out the whole thing, which I should have done to start.
    Furnace was running for shorter than normal periods, and house wasn't warming up, so I figured it was "short cycling". Noticed at the same time that the wireless thermostat was occasionally showing "no signal". none of this felt urgent, because the house was sort of close to the correct temperature most of the day, so the furnace must have been working most of the time.

    LED on furnace board wasn't showing an error, but I followed the procedure in the manual to retrieve stored codes, and it did show a code for "flue limit switch error". Ok, that seems like a common airflow-related issue. Replaced the air filter, checked the combustion air intake, and that's nice and clear. I cannot check the furnace exhaust, as it's on my roof and the roof is covered in ice and snow in that area. I did get on a ladder to look at it, and there's no external blockage anyway. Couldn't be too badly blocked, since it's running fine most of the time.

    So I'm sitting here, thinking that I have two things indicating issues, and I don't know which to troubleshoot. The wireless thermostat (Honeywell THM532R sending to Honeywell TH6320R) seems to be losing connectivity sometimes. AND the flue limit switch is showing an error occasionally. Could one problem cause the other? I don't see how, but .....

    I have called Atco, and they plan to come out sometime next week.

    What am I missing here?
    Quote Originally Posted by ThePenIsMightier View Post
    This quote is hidden because you are ignoring this member. Show Quote
    I'm way less "me" than people give me discredit for.

  2. #22
    Join Date
    Dec 2009
    Location
    Calgary/ALTA
    Posts
    120
    Rep Power
    0

    Default

    Had similar issue with my aunt furnace on Dec, 24, and brought ATCO tech to diagnose as they advised us to replace pressure switch which we did. Problem started again I went to diagnose led light and it was pointing to pressure switch. Call ATCO again and they came after testing indicated that igniter might be faulty and need to be replaced and they did not have one available they recommended ARPIs. Not having much choice called those guys and tech showed up fairly soon. He tested furnace and determined that control board is faulty. Replace it and furnace started to work. Lessons learned, the fault indicator was not working correctly as board was fried and tech even stated that most likely replacing of pressure sensor was not required. If you are troubleshooting furnace follow more advanced methodology using multimeter.

  3. #23
    Join Date
    Jun 2009
    Location
    N/A
    Posts
    2,977
    Rep Power
    22

    Default

    Draft inducer motor, do not have.
    Furnace igniter, do not have.
    Pressure switch, do not have.
    Control board, do not have.

    I think I am thankful for these do not have.
    Will fuck off, again.

  4. #24
    Join Date
    Nov 2008
    Location
    Cochrane, AB
    My Ride
    Trucks
    Posts
    2,122
    Rep Power
    44

    Default

    Quote Originally Posted by speedog View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Draft inducer motor, do not have.
    Furnace igniter, do not have.
    Pressure switch, do not have.
    Control board, do not have.

    I think I am thankful for these do not have.
    Reliable heat is a luxury, and you sir, will have it. I myself have a unicorn, standing pilot and thermocouple with a control board and inducer motor. Made only during the glorious year of 1996.

  5. #25
    Join Date
    Jan 2019
    Location
    The Big Char.
    My Ride
    *The First*
    Posts
    4,188
    Rep Power
    100

    Default

    Quote Originally Posted by Darell_n View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Reliable heat is a luxury, and you sir, will have it. I myself have a unicorn, standing pilot and thermocouple with a control board and inducer motor. Made only during the glorious year of 1996.
    Nineteen! Ninety!! Six!!!
    Nineteen!! Ninety!!! Six!!!!

    Name:  Screenshot_20191230-181847_Firefox.jpg
Views: 446
Size:  35.9 KB

  6. #26
    Join Date
    Jan 2008
    Location
    Upstairs
    My Ride
    Natural Gas.
    Posts
    13,454
    Rep Power
    100

    Default

    So, I don't appear to be having connectivity issues between the furnace and the wireless thermostat any more. That's great! I also haven't noticed the furnace short cycling, but.....

    The furnace is still showing the stored "3-3" code that indicates "flue limit switch error".

    Thoughts anyone, but especially @Darell_n ?
    Quote Originally Posted by ThePenIsMightier View Post
    This quote is hidden because you are ignoring this member. Show Quote
    I'm way less "me" than people give me discredit for.

  7. #27
    Join Date
    Nov 2008
    Location
    Cochrane, AB
    My Ride
    Trucks
    Posts
    2,122
    Rep Power
    44

    Default

    Quote Originally Posted by ExtraSlow View Post
    This quote is hidden because you are ignoring this member. Show Quote
    So, I don't appear to be having connectivity issues between the furnace and the wireless thermostat any more. That's great! I also haven't noticed the furnace short cycling, but.....

    The furnace is still showing the stored "3-3" code that indicates "flue limit switch error".

    Thoughts anyone, but especially @Darell_n ?
    Sounds like a switch that needs to be manually reset. What is your make and model #?

  8. #28
    Join Date
    Jan 2008
    Location
    Upstairs
    My Ride
    Natural Gas.
    Posts
    13,454
    Rep Power
    100

    Default

    Carrier 58STA110 Series 130
    Name:  IMG_20191228_095400653.jpg
Views: 445
Size:  40.8 KB
    Quote Originally Posted by ThePenIsMightier View Post
    This quote is hidden because you are ignoring this member. Show Quote
    I'm way less "me" than people give me discredit for.

  9. #29
    Join Date
    Nov 2008
    Location
    Cochrane, AB
    My Ride
    Trucks
    Posts
    2,122
    Rep Power
    44

    Default

    If it is just a stored code and the heat is working at the time, just cycle the power switch for the furnace to clear the saved code. I would measure the heat rise across the furnace while heating. If it is too high it will trip the '33' code and is likely caused by insufficient airflow. Dirty filter, filter with too high a MERV rating, use of return air filters in the house, too many vents closed off, or the furnace is just oversized for the ducts. Fortunately, you can simply use the next speed on your blower motor as it came wired to heat on the lowest speed. (page 34 in your manual).

    The tech that checks your furnace should be measuring the heat rise and gas pressure before making any changes.

  10. #30
    Join Date
    Jan 2008
    Location
    Upstairs
    My Ride
    Natural Gas.
    Posts
    13,454
    Rep Power
    100

    Default

    Quote Originally Posted by ExtraSlow View Post
    This quote is hidden because you are ignoring this member. Show Quote
    I have called Atco, and they plan to come out sometime next week.
    Hilarious. Atco has declined to do an equipment inspection. According to their email, they are too busy to do this. I'm no longer having issues, so maybe I don't care.
    Quote Originally Posted by ThePenIsMightier View Post
    This quote is hidden because you are ignoring this member. Show Quote
    I'm way less "me" than people give me discredit for.

  11. #31
    Join Date
    Nov 2008
    Location
    Cochrane, AB
    My Ride
    Trucks
    Posts
    2,122
    Rep Power
    44

    Default

    Well, winter hasn’t even arrived yet. There will be -30s very soon.

  12. #32
    Join Date
    Jan 2008
    Location
    Upstairs
    My Ride
    Natural Gas.
    Posts
    13,454
    Rep Power
    100

    Default

    Quote Originally Posted by Darell_n View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Well, winter hasn’t even arrived yet. There will be -30s very soon.
    Negative, I now live here:
    Name:  1616959_landscape.jpg
Views: 384
Size:  69.2 KB
    Quote Originally Posted by ThePenIsMightier View Post
    This quote is hidden because you are ignoring this member. Show Quote
    I'm way less "me" than people give me discredit for.

  13. #33
    Join Date
    Jan 2004
    Location
    Calgary, Alberta
    My Ride
    '91 NA1 ADVAN'D
    Posts
    608
    Rep Power
    21

    Default

    Wow interesting with all these people having furnace issues! My grandparent's H.E. Lennox was having issues starting up this past week. It was diagnosed to be a high-level switch; usually a pretty inexpensive part and easily self replaced. For those having this issue, try looking up your furnace model and find the high-level switch. For the Lennox unit they had, it was a $20 part.

  14. #34
    Join Date
    Jul 2011
    Location
    Alberta
    My Ride
    3.5L 7th Gen Accord
    Posts
    234
    Rep Power
    0

    Default

    I recently had an issue where the furnace would shut off and then cut power to the thermostat and turn it off completely and then the thermostat would reboot (Aprilaire WIFI model). One of the issues with the wireless is that they sometimes they aren't wired properly and after some time, draw more power then they need to and they trip the furnace to turn off. I think what I ended up checking was to make sure the common was wired in so the thermostat would have constant 24V. Wasn't the issue as it was connected. Ended up being a dirty air filter (my fault for not checking it first since I thought I had replaced it about a month ago and it looked pretty clean). Crazy what a dirty air filter will do to the furnace!

  15. #35
    Join Date
    Jan 2008
    Location
    Upstairs
    My Ride
    Natural Gas.
    Posts
    13,454
    Rep Power
    100

    Default

    Quote Originally Posted by Darell_n View Post
    This quote is hidden because you are ignoring this member. Show Quote
    If it is just a stored code and the heat is working at the time, just cycle the power switch for the furnace to clear the saved code.
    Can you clarify how to clear the codes?
    Turning off and back on at the wall switch doesn't seem to.
    Quote Originally Posted by ThePenIsMightier View Post
    This quote is hidden because you are ignoring this member. Show Quote
    I'm way less "me" than people give me discredit for.

  16. #36
    Join Date
    Jan 2008
    Location
    Upstairs
    My Ride
    Natural Gas.
    Posts
    13,454
    Rep Power
    100

    Default

    Reset my flame rollout switches and wasn't showing the error code after. Was showing the 1-1 all clear. Will check it in a bit when it's run a few cycles.
    Quote Originally Posted by ThePenIsMightier View Post
    This quote is hidden because you are ignoring this member. Show Quote
    I'm way less "me" than people give me discredit for.

  17. #37
    Join Date
    Jan 2008
    Location
    Upstairs
    My Ride
    Natural Gas.
    Posts
    13,454
    Rep Power
    100

    Default

    So I'm closing the book on my furnace issues. After a manual reset of the flame rollout switches a couple of days ago, the stored code has not returned. I have no idea when or why that rollout switch tripped. It hasn't happened again.

    I think there must have also been a loose wire on the thermostat transmitter, which I accidentally fixed while checking things.

    Weird that two unrelated things seemed to be happening over the Christmas break. I'll keep an eye on things through the next cold snap.
    Quote Originally Posted by ThePenIsMightier View Post
    This quote is hidden because you are ignoring this member. Show Quote
    I'm way less "me" than people give me discredit for.

  18. #38
    Join Date
    Nov 2008
    Location
    Cochrane, AB
    My Ride
    Trucks
    Posts
    2,122
    Rep Power
    44

    Default

    Quote Originally Posted by ExtraSlow View Post
    This quote is hidden because you are ignoring this member. Show Quote
    So I'm closing the book on my furnace issues. After a manual reset of the flame rollout switches a couple of days ago, the stored code has not returned. I have no idea when or why that rollout switch tripped. It hasn't happened again.

    I think there must have also been a loose wire on the thermostat transmitter, which I accidentally fixed while checking things.

    Weird that two unrelated things seemed to be happening over the Christmas break. I'll keep an eye on things through the next cold snap.
    I would be most concerned on why the heat worked at all with a tripped roll-out switch.

  19. #39
    Join Date
    Jul 2008
    Location
    Pallet Town
    Posts
    817
    Rep Power
    0

    Default

    Just finished minor tune up of my finicky 93% Lennox. Cleaned off flame sensor - check. Vacuumed out that weird nipple at the back of the unit - check. Cleared all air intakes and outlets - check. Thwacked the condensate line with my finger a few times - check.

    Getting ready for this weekends blast.
    Cocoa $8,000 per tonne.

  20. #40
    Join Date
    Nov 2008
    Location
    Cochrane, AB
    My Ride
    Trucks
    Posts
    2,122
    Rep Power
    44

    Default

    Quote Originally Posted by ZenOps View Post
    This quote is hidden because you are ignoring this member. Show Quote
    Just finished minor tune up of my finicky 93% Lennox. Cleaned off flame sensor - check. Vacuumed out that weird nipple at the back of the unit - check. Cleared all air intakes and outlets - check. Thwacked the condensate line with my finger a few times - check.

    Getting ready for this weekends blast.
    We are going to need to see a photo of your weird nipple.

Page 2 of 9 FirstFirst 1 2 3 ... LastLast

Similar Threads

  1. Replies: 13
    Latest Threads: 06-26-2018, 08:57 AM
  2. HVAC Help: Furnace Issues?

    By dj_rice in forum Home and Garden
    Replies: 35
    Latest Threads: 01-03-2014, 11:12 AM
  3. Furnace help!? Any Furnace techs on Beyond?

    By BMDUBS in forum Home and Garden
    Replies: 11
    Latest Threads: 12-13-2009, 12:59 PM
  4. WTB: Furnace

    By MenteL in forum Miscellaneous Buy/Sell/Trade
    Replies: 0
    Latest Threads: 07-29-2004, 04:33 PM
  5. Furnace motor

    By ramminghard in forum General
    Replies: 17
    Latest Threads: 01-30-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •