    Default Circuit Breaker Keeps Tripping with High Load

    Hi All,

    Just wondering if anyone might have a suggestion for me. I live in a Condo and currently have quite a few high draw devices running off the same breaker (Plasma TV, Receiver, Computer, Lamp, and most recently the addition of a 1800W Portable Air Conditioner). If I have everything on, it causes the 15A breaker to trip making everything turn off.

    How can I upgrade the breaker to accommodate for the heavy electrical load on this circuit?
    Originally posted by arian_ma
    your stomach is full of sulfuric acid

  2. #2
    Join Date
    Jan 1970
    Location
    YYC
    My Ride
    1 x E Class Benz
    Posts
    23,635
    Rep Power
    101

    Default

    The breaker is there to protect you from burning your condo down. You can upgrade all the wiring along with it to properly upgrade the breaker, or you can just plug stuff in elsewhere on a different circuit, which is what everyone else would do.
    Originally posted by SEANBANERJEE
    I have gone above and beyond what I should rightfully have to do to protect my good name

  3. #3
    Join Date
    Dec 2004
    Location
    Calgary
    My Ride
    1917 Model T, VW Baja, '18 Ram 2500 CTD/6spd
    Posts
    655
    Rep Power
    20

    Default

    I'm not an electrician, but you need to check what gauge of wire is run, and ensure it is rated for a bigger breaker. If you put 15a rated wire on a 20a breaker, you're asking for a house fire. I'd be tempted to split some stuff off to a different/new circuit, especially if you can put the plug for the A/C on it's own circuit.

  4. #4
    Join Date
    Oct 2006
    Location
    Parked in Baygirl's garage.
    My Ride
    '21 F150 PowerBoost
    Posts
    4,592
    Rep Power
    29

    Default Re: Circuit Breaker Keeps Tripping with High Load

    Originally posted by Neil4Speed
    Hi All,

    Just wondering if anyone might have a suggestion for me. I live in a Condo and currently have quite a few high draw devices running off the same breaker (Plasma TV, Receiver, Computer, Lamp, and most recently the addition of a 1800W Portable Air Conditioner). If I have everything on, it causes the 15A breaker to trip making everything turn off.

    How can I upgrade the breaker to accommodate for the heavy electrical load on this circuit?
    Plug the AC unit in somewhere else, when that fires up, the current draw it makes is huge, and causing the breaker to trip. Just run an extension cord into another room along the baseboard.
    Boosted life tip #329
    Girlfriends cost money
    Turbos cost money
    Both make whining noises
    Make the smart choice.

    Originally posted by Mibz
    Always a fucking awful experience seeing spikers. Extra awful when he laps me.

  5. #5
    Join Date
    May 2006
    Location
    Only 15min from Aspen!
    My Ride
    Nothing interesting anymore
    Posts
    8,440
    Rep Power
    100

    Default Re: Circuit Breaker Keeps Tripping with High Load

    Originally posted by Neil4Speed

    and most recently the addition of a 1800W Portable Air Conditioner). If I have everything on, it causes the 15A breaker to trip making everything turn off.
    Lol, 1800W = 16.36 amps.

    Get a smaller air conditioner.

    Originally posted by spikerS


    Plug the AC unit in somewhere else, when that fires up, the current draw it makes is huge, and causing the breaker to trip. Just run an extension cord into another room along the baseboard.
    If you do this, buy a heavy duty extension. That's a lot of power to draw through a normal household cord for the length you would need.
    Last edited by Tik-Tok; 06-08-2015 at 10:02 AM.

  6. #6
    Join Date
    Dec 2004
    Location
    Calgary
    My Ride
    1917 Model T, VW Baja, '18 Ram 2500 CTD/6spd
    Posts
    655
    Rep Power
    20

    Default

    Also, I think that 1800w A/C would technically require it's own circuit. I'm no engineer and my math skills are only slightly above Mar level, but 1800w/120v is 15a. If your household voltage is below 120v at all, you'll actually be drawing more than 15a. There's power factor and a bunch of other stuff that's admittedly over my head, but my point is that sounds like a device for a dedicated circuit. That and one light bulb should blow the breaker by my marth. Maybe an EE can clarify.

  7. #7
    Join Date
    Jul 2006
    Location
    Victoria Park
    My Ride
    '16 FoRS, '09 UZN215, '90 Z32, '15 Grom
    Posts
    4,139
    Rep Power
    64

    Default

    The 1800W AC alone should be on its own circuit.
    I assume you're running off of receptacles w/ 15A breakers. So split your outlet usages accordingly.

    In regards to changing the breaker, that is also possible but you need to check your conductor size as carson mentioned to see if you can accommodate that larger breaker.

  8. #8
    Join Date
    Mar 2010
    Location
    Calgary
    My Ride
    Ioniq 5
    Posts
    1,834
    Rep Power
    47

    Default

    Originally posted by carson blocks
    Also, I think that 1800w A/C would technically require it's own circuit. I'm no engineer and my math skills are only slightly above Mar level, but 1800w/120v is 15a. If your household voltage is below 120v at all, you'll actually be drawing more than 15a. There's power factor and a bunch of other stuff that's admittedly over my head, but my point is that sounds like a device for a dedicated circuit. That and one light bulb should blow the breaker by my marth. Maybe an EE can clarify.
    Yes and no. It doesn't draw 1800W all the time. It's rated to pull 1800W at peak. This might just be during the initial spike when the compressor starts up or something. Either way it definitely should be on its own circuit.

    @OP I would find a different outlet that is unused and on a different circuit and run a cord over to that. Upgrading a circuit isn't a simple DIY job and being in a condo it's likely not even possible to do legitimately.

  9. #9
    Join Date
    Oct 2008
    Location
    South of Calgary
    My Ride
    is broken
    Posts
    794
    Rep Power
    18

    Default

    Its more like ~112v in Alberta. Every time I have measured it for shit and giggles.

    OP you have too many devices on one circuit. Just run a cord or open a window.

    I would also suggest replacing the breaker if its an older building. Breakers can lose thier accuracy and break too soon if they are getting old. OR if you want to try any burn your house down upgrade to a 20 amp breaker and dont tell anyone ROFL.
    Operator Of Beyond's Official Cardano pool.
    Magical internet money for everyone!

  10. #10
    Join Date
    May 2006
    Location
    Only 15min from Aspen!
    My Ride
    Nothing interesting anymore
    Posts
    8,440
    Rep Power
    100

    Default

    Originally posted by jacky4566
    Its more like ~112v in Alberta. Every time I have measured it for shit and giggles.

    I would also suggest replacing the breaker if its an older building. Breakers can lose thier accuracy and break too soon if they are getting old. OR if you want to try any burn your house down upgrade to a 20 amp breaker and dont tell anyone ROFL.
    I always use 110v when I do the math, that pretty much covers any household situation.

    Also, I was told by a city electrical inspector, if your house burns down, they can actually determine what kind of circuit breaker was in the panel, and can even tell what brand it is. I don't know how true that is, but he noticed a couple of mine weren't of the same make as the rest, and couldn't fail me on them because they weren't part of what his inspection was for, but warned me about that.

    Although OP, if you aren't scared of your panel, I do recommend checking the torque of the screws on the breaker. Last summer my 100amp household breaker kept tripping for no reason, and I found the screws had loosened over time. As soon as I retorqued them, problem solved.

  11. #11
    Join Date
    Jul 2006
    Location
    Victoria Park
    My Ride
    '16 FoRS, '09 UZN215, '90 Z32, '15 Grom
    Posts
    4,139
    Rep Power
    64

    Default

    Originally posted by pheoxs


    Yes and no. It doesn't draw 1800W all the time. It's rated to pull 1800W at peak. This might just be during the initial spike when the compressor starts up or something. Either way it definitely should be on its own circuit.
    The 1800W is the max output when it is running on full capacity, yes. But, this power rating (1800W) does not account for the inrush current you're talking about. If OP can run the AC and not have the breaker trip immediately, we know inrush current is not an issue.

    For OP's situation, it just looks like the connected load is too much for the current breaker size.

    The A/C should be on its own circuit w/ a 20A breaker with the proper conductor sizing.

  12. #12
    Join Date
    Nov 2008
    Location
    Cochrane, AB
    My Ride
    Trucks
    Posts
    2,126
    Rep Power
    44

    Default

    Rule of thumb for compressor inrush is 5x the full load amp draw. You absolutely need an empty circuit for this air conditioner, and even then may occasionally trip the breaker while starting.

  13. #13
    Join Date
    May 2004
    Location
    Calgary, Canada
    My Ride
    958.2 Cayenne Diesel
    Posts
    2,052
    Rep Power
    25

    Default

    Wow, thanks guys for schooling me. This might all be a challenge for me as I don't have anywhere else to Vent the AC other than where my TV and computer etc are.

    I always thought that the breaker was an easily replaceable, and that it wasn't due to the wiring situation. I would really rather not burn down my place so I won't touch anything until I get an electrician in to see what we can do.

    If I just have the AC running (No TV/Receiver but PC), it runs fine without any issues.

    What a pain in the arse haha.
    Originally posted by arian_ma
    your stomach is full of sulfuric acid

  14. #14
    Join Date
    Aug 2011
    Location
    Strathmore
    My Ride
    2005 Dirtymax
    Posts
    2,223
    Rep Power
    22

    Default

    Originally posted by Neil4Speed
    Wow, thanks guys for schooling me. This might all be a challenge for me as I don't have anywhere else to Vent the AC other than where my TV and computer etc are.

    I always thought that the breaker was an easily replaceable, and that it wasn't due to the wiring situation. I would really rather not burn down my place so I won't touch anything until I get an electrician in to see what we can do.

    If I just have the AC running (No TV/Receiver but PC), it runs fine without any issues.

    What a pain in the arse haha.
    Wiring needs to be a specific size to take on the load. You could probably get away with using a 12/3 extension cord as long as its not SUPER long to plug into another circuit.

    When you pop the circuit in your place find an outlet that is as close as possible to where you want the AC and use that with the extension cord.

  15. #15
    Join Date
    May 2004
    Location
    Calgary, Canada
    My Ride
    958.2 Cayenne Diesel
    Posts
    2,052
    Rep Power
    25

    Default

    Originally posted by firebane


    Wiring needs to be a specific size to take on the load. You could probably get away with using a 12/3 extension cord as long as its not SUPER long to plug into another circuit.

    When you pop the circuit in your place find an outlet that is as close as possible to where you want the AC and use that with the extension cord.
    Issue is due to the set up of my place, I'll be running an extension cord a very long (unsightly) way, But if thats what I have to do, thats fine. I also realized the specs were different that I initially thought, so maybe I can move things around a little to accommodate.:

    Input Power 1320W
    Operating Cycle 11.5A
    Originally posted by arian_ma
    your stomach is full of sulfuric acid

Similar Threads

  1. Power tripping bouncer in MA

    By JimmyJones in forum Society / Law / Current Events / Politics
    Replies: 44
    Latest Threads: 02-23-2011, 01:45 AM
  2. Legit ticket or quota-filler? (CPS power tripping content inside)

    By ROBOCOP in forum Society / Law / Current Events / Politics
    Replies: 46
    Latest Threads: 06-22-2010, 09:04 PM
  3. GFI Outlet Tripping

    By sabad66 in forum Home and Garden
    Replies: 5
    Latest Threads: 06-18-2010, 07:52 AM
  4. Brick Breaker High Scores.

    By snowboard in forum Computers, Consoles, and other Electronics
    Replies: 19
    Latest Threads: 12-13-2007, 05:46 PM
  5. WTB Circuit Breaker

    By dgmartinez in forum Miscellaneous Buy/Sell/Trade
    Replies: 0
    Latest Threads: 01-24-2005, 12:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •